Hi, In the datasheet the analog input says
Does this mean you can push the range down to say 0-10V input?
Hi satst5,
You can put the range down to 0-10V by adjusting a(Coefficient) and b(Offset) in ACEmanager->I/O->Configuration.
Example: Your equipment which monitors temperature and it has infomation (If this information is not provided, contact the manufacturer):
0 V is equivalent to - 20°C
10 V is equivalent to 100°C
You will have:
a x 0V + b= –20
a x 10V + b= 100
where: a= Coefficient, b= Offset
After calculating you will have a=12, b=-20. Finally you put these parameter in ACEmanager->I/O->Configuration then apply and reboot gatways.
Thanks,